Omron G9SP & ABB ACS 850 - Safe Torque Off
smtwkla
Dec 2013
Pavoorchatram
I am new to Omron G9SP. I need it to switch an ABB ACS 850 drive's Safe Torque Off (STO). The G9SP contains semiconductor outputs (PNP). Can they be used to switch the STO directly or should I use a relay?
Thanks,
smtwkla
Can be done with / or without a relay. ABB should have a manual specifying criteria & wiring schemes for both methods. Be carful without a relay as some drives have difficulty with test pulses from the safety plc (the manual will spell this out). With a relay it needs to match the safety level of the rest of the safety system.
I would say don't use a relay if you don't need to. The outputs of the GSP9 are rated for safety use so why put another device in the mix...But check your manuals and safety requirements first.
It shows a safety relay. So go with what the manual shows or contact you vendors to see if you can use the outputs from the G9SP directly. Other drives I have used usually show either as being acceptable but since it's a safety thing don't take my word for it.
Hi, My question is about the Omron safety unit G9SP, there is 32 bits on the Red Lion to send information to this safety modue and 32 others bits...
953
I am at a client location where they have the G9SP-N20S on numerous pieces of equipment on a line. I need to make a small addition to the safety...
4,133
I'm installing several Omron G9SP programmable safety controllers in my plant (safety upgrades, ease of troubleshooting, etc) and I'd like to...
3,344
Anybody ever get these two talking over Ethernet? Or at all? I saw that the C-More is FINS compatible but I didn't see anything about FINS-TCP...
1,210
I've come across a system running omeron cx-programmer version 9.42. Am I going to need to find a legacy version of the software to edit and...
53