omron pt and plc not working together

crankshanft

Member
Join Date
Jan 2006
Location
ab
Posts
38
Hi all I have CQM1H and a NS8 on a very simple line i have switch 1 turns on output 1 this works but i need to disable this from the hmi so i added a NC switch after switch 1 and while monitoring the ladder pressing the switch on the PT opens the line but does not turn off the coil.


there is no other control for this coil

Thanks for any help
Tom

Crankshafttemp.jpg
 
Can you attach your program file?

Had something similar to this the other day.
Program section was added after the END instruction,
or was in a JUMP section.

Just a couple of thoughts.
 
The program is quite large, but there is nothing after the end statement nor are any jump statements used. the program has worked/works fine for months now.
I thinking it has to do monitor mode or run mode or something along those lines?
 
all is well don't know why for sure but I downloaded again and turned off the power (don't do this often) and it's working now thanks
Tom
 

Similar Topics

Hi I have a plc omron CJ1M connected to a HMI this is a reconditioned panel in which this plc is connected. But the touch screen of the HMI is not...
Replies
5
Views
3,586
Hi Guys Quite a noob here so please excuse me if I use unprofessional terminology. I've been working on a PLC program for a while now, with the...
Replies
7
Views
3,378
Hi, Dear friends, I have two Omron PLC connected through RS232 Link.First PLC is Omron sysmac CPM2A-60CDT1-D And second is OMRON SYSMAC...
Replies
6
Views
3,567
Hi, Anyone in Omron networking??? see in Hardware we have Omron PLC CS1H CPU66-H and CS1WSCB 41-V1( Serial communication Board with one RS-232 and...
Replies
7
Views
5,611
Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
Replies
4
Views
145
Back
Top Bottom