hi all, hope some of you omron guys may be able to point me in the right direction regards addressing and temp control cards.
the task is simple,build a panel to preheat a packaging machine tool, up to 8 heating zones.
circumstances dictate, i'm using an Omron C200 plc or similar ( we have different models of machine but all use omron plcs), i have never programmed this type (rack)of plc but have skimmed through the manual (500 pages).
from the I/O table in CX programmer, IR000 inputs, IR001 outputs, IR002/3 temperature control cards.
if i was using a standalone plc for one zone, i would likely write
IF I0.0 (zone 1 selector switch), MOV DW(temp control input) TO VM100 (variable memory 100).
IF VM100 <= 12345 THEN SET O0.0. (Heater on).
could someone perhaps translate that idea to cx programmer, im unsure about addressing the temp cards, also, should i be using, compare floating point data???
many thanks.
the task is simple,build a panel to preheat a packaging machine tool, up to 8 heating zones.
circumstances dictate, i'm using an Omron C200 plc or similar ( we have different models of machine but all use omron plcs), i have never programmed this type (rack)of plc but have skimmed through the manual (500 pages).
from the I/O table in CX programmer, IR000 inputs, IR001 outputs, IR002/3 temperature control cards.
if i was using a standalone plc for one zone, i would likely write
IF I0.0 (zone 1 selector switch), MOV DW(temp control input) TO VM100 (variable memory 100).
IF VM100 <= 12345 THEN SET O0.0. (Heater on).
could someone perhaps translate that idea to cx programmer, im unsure about addressing the temp cards, also, should i be using, compare floating point data???
many thanks.