CAUTION: This will be a long post.
Please give me some light, I am so lost with the omron temperature controller that we are using to proportionally control a motorized valve.
We have a steam room, where parts are being tested. The room has to be maintained at 75, 85 or 95 deg. C depending on the parts. Since we are aiming for a proportional control, I was expecting the movement of the valve will be in proportion to the difference of the SV & PV. Hence, if SV-PV = 10%, valve movement is 10%.
My motorized valve responds to 4-20mA and judging from the wiring diagram of the temperature controller (see manual1 pic), I can only connect it to the transfer output. However upon checking the manual, this transfer output has generally 3 functions (see manual2 pic): Set point, PV & valve opening. Our motor valve does not have a potentiometer, hence we cannot use the valve opening function.
Upon testing, we found out the ff:
1.) Set point function --> the valve opening is proportional to the value of the set point. Hence, if set point is 85 deg. C, valve opening is 85%. The valve opening does not change as long as the set point remains the same.
2.) PV function --> the valve opens & closes in proportion to the actual temperature. Hence, if actual temperature is 50 deg. C, valve opening is 50%. If actual temp increases, the valve opening increases while it closes with the decrease of the latter.
This controller does not seem to make any sense. Has anyone use this controller? What am I missing out with this one?
Please help.
Please give me some light, I am so lost with the omron temperature controller that we are using to proportionally control a motorized valve.
We have a steam room, where parts are being tested. The room has to be maintained at 75, 85 or 95 deg. C depending on the parts. Since we are aiming for a proportional control, I was expecting the movement of the valve will be in proportion to the difference of the SV & PV. Hence, if SV-PV = 10%, valve movement is 10%.
My motorized valve responds to 4-20mA and judging from the wiring diagram of the temperature controller (see manual1 pic), I can only connect it to the transfer output. However upon checking the manual, this transfer output has generally 3 functions (see manual2 pic): Set point, PV & valve opening. Our motor valve does not have a potentiometer, hence we cannot use the valve opening function.
Upon testing, we found out the ff:
1.) Set point function --> the valve opening is proportional to the value of the set point. Hence, if set point is 85 deg. C, valve opening is 85%. The valve opening does not change as long as the set point remains the same.
2.) PV function --> the valve opens & closes in proportion to the actual temperature. Hence, if actual temperature is 50 deg. C, valve opening is 50%. If actual temp increases, the valve opening increases while it closes with the decrease of the latter.
This controller does not seem to make any sense. Has anyone use this controller? What am I missing out with this one?
Please help.