Disclaimer: This might be simple - about to have my first grandkid any day now so I'm up late with my daughter and VERY sleepy during the day so my brain is lagging way behind its usual substandard.
Working with a PLC-5. Trying to calc Duty percentage of a pump. Looking for short cycling, not looking for a runtime.
The math is easy: duty% = [Running time] / [cycle time]
Haven't had to do this particular thing before and it caught me that this isn't dead simple, but again, substandard brain.
I haven't tried an OSR yet, I will while I wait for an easier answer, but how else can you time a single bit from true transition to true transition to get the entire cycle time?
For the run time use a tl timer while it is running and copy the accumulated value when the timer is deenergized. Perhaps a retentive timer.
For the total time it depends. Is the process cyclical or is it 24/7 Like a water treatment plant.?
That would catch the running time, But I need to get the cycle time (On time + Off time)
Its 24x7 as needed, no regularity to it. I also have to have 2 time scales depending on which process it being done. One takes minutes, the other takes
So you want time between true transitions. You are dead on using a OSR.
Rung 1 - OSR Logic
Rung 2 - OSR bit true = MOVE Run Timer.ACC to Storage to capture data
Rung 3 - OSR bit false = Run Timer
This will capture time between OSR Pulse. When OSR transitions to true it will capture data. The next rung will reset timer. The next Scan Cycle Timer starts accumulating next cycle time.
P.S. Congratulations!! May it be healthy and happy.
Rung 1- XIC Pulse trigger - ONS - OTL (Latch Bit)
Rung 2- XIC Latch Bit - MOVE Cycle Time.ACC to Storage to capture data
Rung 3- XIO Latch Bit run TON Cycle Timer
Rung 4- XIC Latch Bit - OTU Latch Bit
This will keep latch bit true for 2 rungs to Move Data and reset Timer.
That should do it. I got the idea. I kept thinking bits didn't resolve until the end of the ladder (like I/O) I know better so thats my problem today.
Man I need a nap !
Thanks for the help.
Man I need a nap !
Don't be afraid to. Yea, there are times you have to push through, but I've done it. 19 hours into a job I told them I'm going to take a nap. Wake me in an hour. No point to continue if my brain is useless.
Hello..I am new to Plc.I have Mitsubishi Melsec Fx3Ga-40MR PLC controlling a machine for packing powder.Currently the Plc has issue which power...
143
Hi, I have a 1500 that controls a station with diferents warehouses, but i also have a 1200 that controls one of those warehouses, i have been...
280
A couple days ago I accidentally toggled an alwasyoff bit. The issue is it was set up as a single OTU on a rung, nothing else, and used as XICs...
227
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
18
1,019
How i Can connect Delta plc, with Beckoff remote IO cards?
174