Well, that is actually over complicating things. Getting down to the absolute basics, pull out a block diagram of an old (but not ERC Old) analog DC drive.
Closest to the motor (control wise, not SCR wise), is always a current regulator, which takes a setpoint and feedback. True, for winder applications, or tension control, I'll often just inject my command signal to the setpoint channel of the current regulator. In a typical drive, the next outer loop is the actual speed regulator, which again has a setpoint and a feedback. The output of the speed regulator directly becomes the command input to the current regulator (ignoring current limit controls for now).
On a DC drive and motor, with a fixed field, armature current is directly proportional to torque, which is why it generally works so well for winders and such, since the speed loop is normally much slower then the current loop. Even more generally, each time you add another outer loop, you introduce more lag into the system, as each outer loop must be slower then the loop it's feeding for stability.
Modern AC drives, with intelligent vector control, or ABB's direct torque control perform wonderfully when directly controlling the motor torque. Of course, that didn't work so well in the 6 step drive days :)
Dan, don't you ever sleep?
Hoot hoot.
OK the DC application I can understand pretty quick.
The VFD application without a special torque module I got a little difficulty with. But a vehicle is not a winder - thankfully I think.
Thanks for the help.
Dan Bentler
How many motors we operate from single drive? I have 4 motors of 1hp, all motors have same function. Is it possible to run all 4 motors from...
16
5,272
I have 3 waist High Conveyors in a line that each have a 1.5 HP 460 motor each has a 140M-C2E Breaker/MOL & a contactor. Can I put a single VFD...
3,697
Here is the situation: I want a VFD to control a Fan motor - but I have a redundant fan that should not be used unless I am servicing the main...
23
8,581
Hey guys , I am involved in a equipment installation process wherein the customer wants me to run multiple motors with a single VFD. I...
2,083
I have been looking at a couple of power tools that have a 220v 3 phase motor. I was wanting to avoid having to install a rotary converter. But I...
2,277