Hi
I have come across a Small problem in my Network Set up, it consisits of a CS1 rack PLC with 2x Controller links and 1x Ethernet unit called Network 1,2,3 (networks 1,2,3 configued using CX integrator Routing tables ) if you are reading this then you undstand what I mean (( if more than one Comms unit is installed in a CSI, CJ1M plc unit then there has to be Networks created in order for them to WORK))
any way on to the problem
CS1 PLC has 2 controller links installed lets call them network 1 and 2..
Network 1 has 28 C200H plcs using controller Link to Comunicated with them a1l Auto configured and working OK passing info back and forth..
Network 2 has 3 CJ1M installed all auto configured, but each CJ1m will talk to each other and allow me to configure any settings in any plc in the network 2,,
the Master plc CS1 Contoller link will see all PLCs BUT WIL NOT allow me to edit any the CJ1M plc on network 2 and when you do a Diagnostic check all the 3 CJ1M plc fail the test, although they can be seen on the network ??
Basically the CS1 controller link will not read any info from the Network, but the CJ1Ms will read and write ok between but not read or write to the CS1 controller link,,
I have not set the Routing tables to Pass threw any PLC only created 3 networks for the Comms card to work in the CS1 plc
if you are a PLC programmer with network experence you wil know what I am doing
Thanks for reading and sorry to boar you
Ian
I have come across a Small problem in my Network Set up, it consisits of a CS1 rack PLC with 2x Controller links and 1x Ethernet unit called Network 1,2,3 (networks 1,2,3 configued using CX integrator Routing tables ) if you are reading this then you undstand what I mean (( if more than one Comms unit is installed in a CSI, CJ1M plc unit then there has to be Networks created in order for them to WORK))
any way on to the problem
CS1 PLC has 2 controller links installed lets call them network 1 and 2..
Network 1 has 28 C200H plcs using controller Link to Comunicated with them a1l Auto configured and working OK passing info back and forth..
Network 2 has 3 CJ1M installed all auto configured, but each CJ1m will talk to each other and allow me to configure any settings in any plc in the network 2,,
the Master plc CS1 Contoller link will see all PLCs BUT WIL NOT allow me to edit any the CJ1M plc on network 2 and when you do a Diagnostic check all the 3 CJ1M plc fail the test, although they can be seen on the network ??
Basically the CS1 controller link will not read any info from the Network, but the CJ1Ms will read and write ok between but not read or write to the CS1 controller link,,
I have not set the Routing tables to Pass threw any PLC only created 3 networks for the Comms card to work in the CS1 plc
if you are a PLC programmer with network experence you wil know what I am doing
Thanks for reading and sorry to boar you
Ian