Guys, looking for some help at a customer site...
I need to add open wire detention to a system using 1794-IE8 and 1734-IE4C modules.
For the 1794-IE8, it's configured as 4-20mA mode. (Under-range does not apply to 0-20mA mode).
Originally, I thought piece-o-cake. Just look at the under-range bits and trigger errors off of that. Well, shame on me for thinking life can be so easy. Turns out that the under-range bit is triggered when the signal is AT or below 4mA. Well, I have a few pressure transmitters which are loop powered. 4mA = 0 PSI, and at an "IDLE" state the transmitter is putting out 4mA and the under-range bit is being set. This is clearly not a broken wire situation, therefore I cannot use this as a broken wire trigger.
I have not looked too deep into the 1734-IE4C cards yet, but I assume a similar situation may occur.
Open to suggestions on how to detect an open wire w/o false triggers, basically trying to reliably detect if I have a bad 4-20mA analog transmitter.
Hi
How about if you set it up as a 0 - 20 then change your scale to suit let's say 0 ma = - 20 and 20 ma = your max. You will have to change the scale to shut your range.
Now when you get a- value you know you have a wire break.
Donnchadh
Looks like that is what I will have to do...just made my days a little longer. But at least I learned something today!🍺
Hi
You could set up a scaling aoi and add the you need in so at least you only write it once and it might make the days a little shorter
Donnchadh
We have AOI's that handle all the scaling, it's just that I have to do this while the plant is operating, so I have to be selective and take my time with it.
Actually went a little quicker than I thought, it also affected my PID loops to so I had to make sure it was ported across everything.
Good times, hopefully that's my biggest hurdle of this trip.
calibrate the sensors a little higher like 4.4 mA
and at the top use 19.6 mA.
this way the broken wire detection will be good. and in the PLC you will have to make a conversion to get the numbers correct again with a span and zero.
Thought about that for a minute and quickly dismissed it. They have a calibration crew come in every 3-6months to calibrate all their sensors. Last thing I need to do is provide documentation and reasoning for such an odd zero and span.:sick:
Reconfiguring the IO ensures and replacement devices will just "work" regardless of the zero/span settings (well, assuming they configure it 4-20mA).
Hi Guys, For Allen-Bradley 1756-OF8 module, the channel status word has a bit for open wire detection "ChxOpenWire". I checked for the 1756-OF8I...
2,376
I'm working on troubleshooting a PLC for a piece of manufacturing equipment. The issue I'm trying to resolve is an open wire fault not getting...
553
i have 2 backups: *.PVC and *.pvd file types thanks in advance for any help
162
hi All Can you please help me to find the right software to open Zip backup of 434 12A PLC? Any major steps I need to know when opening? Regards
106
194