Opinions on methods
g.mccormick
Jul 2012
IN
961
I would like to use this thread to ask for opinions on methods/practices. I am starting on a fairly large complete rewrite of code for several systems and I would like to "do it correctly". So, I ask for some opinions here.
1. I have an AOI for dealing with analog inputs. This AOI does scaling, filtering, alarming, etc. The systems I am working on have between 16 and 64 analog inputs. Do you have individual instances for each AOI call, or just reuse the same instance? I can see an argument for each way. If individual instances and you're not using in a loop, I can see the values in code for each instance. This could help with troubleshooting, but I also can/will have the AOI data type be equal to my analog input data type and pass by reference.
If I just use one instance, I save creating a lot of unused tags.
More questions will come as I think of them.
I believe best practice would be to have an instance of the AOI for each analog input. As LD said, I'm not sure how it would work otherwise.
The number of tags you need will depend on how much configuration you give down the line.
If the same filtering would work for all analogs then you can encapsulate it within the AOI (no external tags required). If you want to configure the filtering at startup but don't want to give the ability to change it later through the programming then you can send constants into the AOI instances at startup. If you need the ability to change the filtering pragmatically later then you would need to assign tags to your filter parameters.
Likewise with the scaling.
If you want tags for everything, then I would look to using arrays and possibly arrays of UDTs to make things easier to look at in the program.
Not familiar with AOI but if you re-use the same instance will the filtering still work?
Yes. The INPUT/OUTPUT UDT holds the values and is passed by reference. The AOI grabs the last value first before doing any scaling etc.
// AOI to scale an input, filter and limit its output.
// First we want to remember the last output value. Used in the filter calculation.
LastEngVal := UDT_DataTag.Engr_Val;
LastSigVal := UDT_DataTag.Signal_Val;
I think the use of an AOI (FB) as one instance is fine providing things like filtering etc. is passed both ways i.e. IN/OUT parameters, the idea is that you debug the code in the AOI before using it in earnest so there should be no need to look at it again if it causes problems then you have not tested it properly as it should work the same for all calls. If there is a problem then just create a separate instance and find the problem. In saying that, I see no reason other than saving program memory not to have separate instances. In actual fact all an instance is just a macro in effect (saves you typing).
Use a single AOI once for every analog input
Pass a UDT tag containing all required scaling/alarm setpoints etc where each UDT represents an analog input and all its properties
This tag structure will become the equivalent of the siemens DB
Yes I planned to define the AOI with UDT as inout parameter. That is currently how I have it.
The thing that bugs me about having an instance each, other than wasted tag space is that effectively all of the data is in two places. The values are in the AOI data tag and in the the In, out, and/or In/Out tag/udt.
I guess that does pose a new question, does anyone just name/use the AOI tag as the "main" tag?
Just to clarify, you are saying only one instance reused correct?
Here's what I would do. This is definitely a simplified version of what you describe (and hasn't been tested) and is in CoDeSys but the ideas apply.
Define a UDT with the filtering and scaling parameters
Code:
TYPE AnalogParameters :
STRUCT
	rFilterTimeConst:	REAL;
	wScale_In_Min:		WORD;
	wScale_In_Max:		WORD;
	rScale_Out_Min:		REAL;
	rScale_Out_Max:		REAL;
END_STRUCT
END_TYPE
Define an AOI (Function Block)
Code:
FUNCTION_BLOCK AnalogConditioning
VAR_INPUT
	wRawValue:		WORD;
	udtParam:		AnalogParameters;
END_VAR
VAR_OUTPUT
	rScaledValue:	REAL;
END_VAR
VAR
	rThisScaled:	REAL;
	rLastFiltered:	REAL;
END_VAR
// Scale the value - Check for division by zero
IF (udtParam.wScale_In_Max-udtParam.wScale_In_Min) <> 0 THEN
rThisScaled :=	udtParam.rScale_Out_Min +
				wRawValue * (
				(udtParam.rScale_Out_Max - udtparam.rScale_Out_Min)/(udtParam.wScale_In_Max-udtParam.wScale_In_Min)
ELSE
	rThisScaled := 0.0;
END_IF
// Filter the value and save last for next iteration
rScaledValue	:= rLastFiltered + udtParam.rFilterTimeConst * (rThisScaled-rLastFiltered);
rLastFiltered	:= rScaledValue;
Define arrays for everything in the program and call in a FOR loop. Note that the maintenance guys are going to hate this method. Individual calls would be much more visual and allow you to see the values in the program vs. having to monitor the tags to see them. But you seem to want to minimize typing so
Code:
PROGRAM Main
VAR
	Analogs:	ARRAY [1..10] OF AnalogConditioning;
	AnalogParam:	ARRAY [1..10] OF Analogparameters;
	wRawAnalog:	ARRAY [1..10] OF WORD;
	rScaledAnalog:	ARRAY [1..10] OF REAL;
	iIndex:			int;
END_VAR
FOR iIndex:= 1 TO 10 DO
	Analogs[iIndex](wRawValue:= wRawAnalog[iIndex], udtParam:=AnalogParam[iIndex] , rScaledValue=>rScaledAnalog[iIndex] );
END_FOR
If I were the one doing the troubleshooting, I would prefer one instance of the AOI for each signal. Of course you will likely encounter some of my kin folk that will ask,
"AO what?" I apologize in advance on their behalf.
Bubba.
An AOI for each input would be the best way to go
But why the analog cards / modules have all that built is you just have to set it up
I can't believe you can do it better in an AOI then then can in hardware
Good morning all. I'm working on a rehab where they had a standalone InTouch 2014 HMI that they called a SCADA, but it's really basic stuff. The...
183
Hey guys. We've been learning Ignition and going through all the courses on Inductive University. I really like the software and the things you...
20
1,157
Anyone use WEG vfds on here? Thinking of trying CFW300A01P6T2NB20.
771
Looking into using a Stride Managed network switch in an upcoming build versus a Stratix 5700. Just looking for others experiences, comments or...
4,979
With the Automation Directs Open Source Arduino Compatible PLC and the Open plc Project, plus all the Raspberry Pi HMI's, what are your opinions...
4,326