Hi
I need to interface supply air pressure into the emergency stop which is a monitored 2 channel circuit
I have googled but does anyone know of a double pole switch preferably force break contacts and CE marked
Cheers
You may use only one contact for example in the fase line, and have the estop both in Phase and Nul line.
as this switch is not emergency, (there is a safetyvalve in the circuit.
Hi
Shooter .. I considered a single pole in the circuit for A1 but this would not have any redundancy... so I want 2 contacts in the e-stop line so a failure of 1 contact would cause an estop and therefore be safe.
Thanks for the other suggestions I will check them out tomorrow.
Cheers
Hi
Just a thought, but this sounds like you might actually want to use 2 unique pressure switches.
What happens when the MECHANICAL component in the P-Switch fails? Both contacts still report true, but you have no air pressure.
In my experience, pressure switches fail every 3-5 years.
I can only speculate that they just become accustomed to being in the "engaged" state, and will not de-energize without a tap from a wrench.
If this is for a safety circuit too, make sure you bring in a test procedure for this/these switches. Just my experience :p
Hi Devo
That is why I was looking for a force break type which I am starting to think doesn't exist..but ty for the headsup anyway
I apologize in advance if this is off-topic, but I really need to understand what's going on... While doing some renovations, it was found...
20
5,581
What is the simples way to do a double click of a button in a ladder logic. New here and I hope this has not been asked before.
22
541
Hi All, I'm keep getting double quotes in between selections rather than the beginning and the end. Here's the script and please help to find...
806
Hi! I am using a TM200CE40T PLC from Schneider to write data over Modbus. I have used Memory words (%MW) before using the Write variable...
541
Hello All, IÂ’m starting a new project where the plc is connected throught LAN with external software which write some data on PLC db, obviously...
520