Keith,
If you are installing in France ypu ned to check what type of power/earthing system will be used to supply the machine. IT supply is quite common in france; this is where star point of the transformer is not earthed. http://en.wikipedia.org/wiki/Earthing_system#IT_network
A single fault to earth/ground will not trip a breaker but will cause there to be a potential difference of line voltage between the other two phases and earth/ground. In an IT system you must detect this first fault. http://www.bender-us.com/knowledgebase/?a=ground-fault-detection-ungrounded-system
In addition you should be aware that many VFDs don't like IT systems and it is for this reason that one of my current projects being installed in France has a 500KVA isolation transformer.
Nick