Output 5v to 24V
The program that I did works correctly, is loaded in the PLC correctly. The PLC does not mark mistakes and does not alarm. The LEDs in the Output Unit ignite well, but it does not give voltage, already check with a multimeter and it measures 0 volts
I don't know if the Output Unit has to be configured or that it should do.
i need HELP
Have you wired a positive and negative to the output card where shown?
If I remember correctly, the OD212 is a PNP type output. Is the common to the coil of the relay negative?
I would also suggest you use a relay with a flywheel diode fitted to protect the output from surges.
The card does not need configuring.
Fernando,
be sure to measure the voltage between the positive voltage rail and the output. BobB is right, the OD212 is a PNP output card, so the relays should have the positive voltage rail as common. You can see this in the picture from the CQM1 operation manual I've attached.
Kind regards,
hello ... i facing a problem with I/O unit for omron c200he..whereby the output bit can be triigger ON..but i cant the external relay on .. i...
2,152
We're having extreme difficulties getting the PLC to recognize the High Density Output Module (C200H-OD218). We're using SysWin 3.4 for...
11,472
Hey all, I am starting a new project for a customer and I am adding in solenoid valves. Once added, I noticed there was a lack of an Output...
78
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
172
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
114