Overflow Trap Placement
Tim Ganz
Dec 2010
Dallas, Texas
700
I have a SLC 5/05 application that keeps faulting every couple weeks to a math overflow.
In the logic there is a math overflow S:5/0 on an unlatch instruction in the main ladder LAD 2 but it is above about 20 JSR instructions that call other subroutines.
Should this be overflow trap be located after the JSR's and be just above the end instruction?
I am thinking with it above the JSR's it is only protecting the logic in LAD 2 but if I move it below the JSR's and place it just above the end instruction it will protect the entire program?
Am I correct on this?
Hi Tim
That is correct.
It may be worth looking through your data files when the plc is faulted to see which one is causing your problem. It is not always easy to find but it's always with a look for a value that's above 32000
Donnchadh
Yes, the best position for that logic is at the very end of LAD 2. You can still have additional logic to monitor the separate overflow bit so you can still do something about the math overflow. This unlatch just prevents the controller from faulting because of the overflow trap bit.
OG
I would use the over flow bit to latch a unique coil and reset the overflow bit after every divide. This way you know where the overflow occurs and can fix it.
There are many more instructions which can set the Math Overflow status than just divide instructions. And of course all of them will set the "trap" bit when overflow occurs.
FWIW, Logix500 is the only "family" of A-B processors that has the additional "trap" bit, which, if still set at the end of the scan, causes a major fault. Perhaps someone thought it was a good idea, but has been dropped again in Logix5000, so clearly not a great idea.
I am just so used to seeing OTU S:5/0 as the last rung/instruction in a Logix500 program. Any math overflow that is significant in an application should have been dealt with as it occurred, not at the end of the scan. Any "damage" that could be attributed to math overflow has already been processed, up to the end of the scan.
Summary - put an unconditional rung with OTU S:5/0 as the last rung of file 2. Deal with any arithmetic status bits as required, for each "important" piece of code.
Hi Gurus I have an issue with 2 similar programs. One faults and the other doesnt. When i enter a number on the HMI larger than 546 ( MUL x 60 =...
3,430
Hi I need help solving this Fault Code 20h (Math Overflow Trap S5:0). I download the code into the ML 1400 PLC. When choosing RUN it gives me a...
22
17,309
I'm re-writing some Logix500 code in Logix5000. The original programmer is unconditionally unlatching the S2:5/0 Overflow Trap flag in the Main...
2,905
Hi All, playing with a Micro850, and on last transfer of the program to the PLC, fault with code 0xF860. Description is "data overflow occurred"...
3,427
We are getting a fault...... Math Overflow Trap S:5/0 = 1 Apparently we are getting a value greater than 32767 or less than -32766. If...
7,847