Panel view 1000 Devicenet to DH+ Change
controlconcepts
Oct 2008
boston
300
I have a PV 1000 T10C10 Ser B That has from the factory the DeviceNet communication card installed. I am wondering if it is possible to change the Comm card out to a DH+ one. I am think the firmware may have to be upgraded to have it accept the new Comm card. Is this at all possible or Has any one don this? I thought I saw a post or a document on this but that was some time ago.
Thanks, Matt
One other thing I was wondering is the DeviceNet port the only way for the PV to communicate to a PLC or can you use the DF1 port to connect to the PLc?
Devicenet is the only way to communicate with your PLC.
The RS232 port is for upload/download of its program or it can be configured for a printer. It cannot be used to communicate with a PLC.
Thanks, Micky. That's what I thought.
Dose that mean swapping out to a DH+ card is out of the question or just for the DF1 port?
Even though the hardware is physically modular, you cannot change the communications daughtercard on a PanelView Standard terminal.
If you attempted to load the firmware for a 2711-T10C8 (DH+) into the terminal, it would identify that the terminal is a -T10C10 and wouldn't accept it.
2711-t10c10
You cannot do that.
This motherboard is keyed to be a devicenet motherboard & it will fault with any other type of communications port.
I purchased a used PanelView Plus 1000 to learn get familiar with the software. Seems to be a pretty popular HMI. I can ping the HMI but I cannot...
893
Hi ya´ll! I want to take a backup on the HMI and opened up Factory Talk View Studio - View Machine Edition v12.00. First thing i notcied was...
1,351
When I see the Kilogram data on the electronic scale indicator that changes quickly and smoothly, but Same data on panel view plus does not change...
1,274
Hi; At our one of machines, there is Allen Bradley panel view 1000. The HMI was working fine but after a power cycle, it failed to build...
4,600
I have a customer who has multiple PV Plus 1000's. These run Firmware 5.1 and Window CE. I need the serial numbers off of the software that is...
1,540