Panel view Plus 1000-real time data issue on the screen

sinanmoral

Member
Join Date
Apr 2020
Location
Istanbul
Posts
52
When I see the Kilogram data on the electronic scale indicator that changes quickly and smoothly, but Same data on panel view plus does not change as quickly as weighting scale indicator.
Communication between PLC and Scale weighting indicator is Ethernet IP.

I wanna see real time data on the panel view plus 1000 like weighting scale indicator.



Thank you in advance.
 
Each display (screen) has a configurable update rate. The default update rate is 1 second. This is fine for most applications, but if you do need a faster screen update you can change it. Of course, faster updates mean more network traffic, so you want to think about, "how fast do I really need this to update?" We don't always just choose the fastest update rate.

Changing this setting requires FactoryTalk View Studio. It cannot be changed at the PanelView. So you would have to make the change in Studio, save it, create the runtime, then download the runtime.

OG
 

Similar Topics

Am asking if we can upgrade sd ram and cf card of panel view plus ab by a normal sd ram and cf card but Allen Bradley to save cost because in ab...
Replies
9
Views
281
Good morning, I have a question, I would like to know if I can send an Excel file to an email from my panel view and see how it is possible to...
Replies
1
Views
159
I want to run a factory talk view ME project in a Panel View Plus 7 Performance HMI. The project was developed in a 'Windows 7 Professional 64 bit...
Replies
5
Views
334
I purchased a used PanelView Plus 1000 to learn get familiar with the software. Seems to be a pretty popular HMI. I can ping the HMI but I cannot...
Replies
6
Views
890
Hello, hope yall are doing well. I have a HMI program where I need to add a "GoToDisplay" button, so when this button is pressed, it goes to a...
Replies
5
Views
889
Back
Top Bottom