I am converting a Panelview 1000 to a Panelview Plus 1000, connected to a MicroLogix 1500. When doing the conversion, I received a Bit Array error. This would usually be a simple work around but the array is writing to S:1/0-4. They do this to allow the HMI to control Program Mode (1), write to EEProm(14) and Run Mode(6). I was able to create a new HMI tag and write the value to an integer in the controller, but I cannot write the value to the first 5 bits of S:1. Am I missing something? Is there a work around for this? ANy help is appreciated.
I am converting a Panelview 1000 to a Panelview Plus 1000, connected to a MicroLogix 1500. When doing the conversion, I received a Bit Array error. This would usually be a simple work around but the array is writing to S:1/0-4. They do this to allow the HMI to control Program Mode (1), write to EEProm(14) and Run Mode(6). I was able to create a new HMI tag and write the value to an integer in the controller, but I cannot write the value to the first 5 bits of S:1. Am I missing something? Is there a work around for this? ANy help is appreciated.