panelview 1250 trend/datalogging problem

jimpad

Member
Join Date
Sep 2004
Location
Paducah, KY
Posts
88
Normally my trend works fine... I can open a new display, go back to the original display and the trend is redrawn with historical data. Occasionally, when I go off the display and come back the historical points are gone the the trend only draws new data. One thing I noticed, is upon powerup of the panelview when the datalog model "general" is started there is a small yellow triangle with a red mark in the middle. If I cycle power on the panelview the problem is fixed for awhile.

Any help appreciated.

Jim
 
I've had this problem before where on startup the PV Plus datalog fails on startup. I'm not sure if this is due to a battered ethernet network or finicky firmware. Seems like it takes the PV Plus a while to connect to the PLC's on the network. When I see this on startup I just go back to the PV setup screen and hit the Run Project pb again and it starts up with out a problem.
 
It's been a while since I've looked at it, but I believe so. I think it says datalogging failed to start with a bunch of other warnings and tag errors. It seems as though the startup error timer time's out before a connection is made with the PLC. It's especially bad with processors that have a small overhead timeslice <20%. If you can afford a higher OTS in your processor you will see improved communication to your PV Plus.
 

Similar Topics

Hey guys, I'm at a bit of a loss with a problem I'm having with some PVP 1250s and hoping for some advice. In firmware and application version...
Replies
0
Views
302
Hello team I have any issue with the AB PanelView 6 1250 with 11 firmware install We have 8 in total and about 6 of them if you reboot them or...
Replies
4
Views
1,483
is it possible to comunicate a powerflex 753 (ccw) using ethernet 20-750-ENETR card to a panelview plus 6 1250 (factorytalk view studio me)...
Replies
0
Views
1,503
Hi all, I have an ihm and I need to connect this with compact logix PLC. In factory talk this communication works well (factory talk and fisical...
Replies
1
Views
2,343
Hello, I recently installed an **** Flexy 201 so we could monitor our PLCs (one SLC 500 and one Control Logix) remotely under a VPN. One of the...
Replies
0
Views
2,371
Back
Top Bottom