Panelview 300 communication
w0lfie
Jul 2007
Cut and Shoot, TX
I am trying to download a program to a PV300 Micro (M3A18L1) that already has a program on it (bought it used). RS Who happily reports the PV, and the COMM light is on in the diagnostic screen. So I'm pretty sure all of that is set up correctly. Hopefully I'm just missing something obvious.
Here's the setup in RS Linx:
Device Name: AB_DF1-1
Comm Port: COM8
Device: SLC-CH0/Micro/PanelView
Baud Rate: 19200
Station Number: 00
Parity: None
Error: Checking: CRC
Stop Bits: 1
Protocol: Full Duplex
From the computer, I'm using a standard USB to serial (works fine for connecting with PLC), and then the usual AB communication cable. The cable's part number has been missing for a while, but it works with the PLC, too.
The settings in the PV exactly match the configuration in RS Linx. Also, the Comm circle is filled in and the Fault circle is not. It also says connected.
Setup in PanelBuilder32:
X - Automatically use RSLinx if available
Internal DF1 Drivers: (what are these?)
COM4 - Rescan COM Ports does not change this
Configure Internal DF1 Driver has the same info as above.
Hardware handshake is not checked off.
Report from PanelBuilder32:
X - Identifying operator panel
Error 2416 - No ACK received
Verify your cable connections
If you are using a direct connection to a PanelView via DF1, insure that the PanelView does not have its printer port enabled.
I get the same error if I try to upload the program off of the PV.
Off-topic: they misspelled "ensure" as "insure."
nevermind
I figured it out. There's a drop down box I didn't see. Transfer type has to be set to Point-to-point RS Linx. That seems odd, since I had "Automatically use RS Linx" selected in the workstation setup menu.
Oh well, mystery solved.
I have three machines that are fairly identical and we wanted make a backup of the programs from the PanelView 300 Micros, 2711-M3A18L1 for each...
20
8,967
Hi All, Currently There is Panelview 300 Communicating with 1794 Flex Processor L34 on RS 232 Port (DH 485). The Flex Processor will be...
2,630
Does anyone know the steps involved in getting kepserver to allow communication from an IDEC Microsmart PLC to a Panelview 300?
2,921
I am having pvc300 with me. I created my new program in ccw. The issue is that after clicking discover in ccw my hmi is not showing up there. Any...
151
merry christmas and happy new year i have a click c0-00dr-d and allen bradley 2711c-t3m. can the panelview talk to the click plc via modbus...
231