Is this the clock battery flat?
Does anyone know how to remove the back of the PV 300 micro. Is it possible to replace this battery. AB says it's not user replaceable but of course they would say that
 
As far as I remember no parts are user replaceable in the 300, the back is not supposed to be removable, there are two possibilities, the RTC clock chip may have it's own battery (would require a new chip as it is encapsulated) or the built in backup battery is flat, I do believe that error 32 does refer to the RTC.
 
Per the manual, self test error 32 is the real time clock. It also says the battery has an expected life of 7 years and is replaceable EXCEPT for the 300 Micro.



My last facility had some of those in service and had a battery fault on a spare unit we tried to install. After investigating repair options some, we opened it up and everything was encapsulated/potted to make it non-serviceable (by us). It may be possible to dig into it and find which bit is the battery and replace it, but it's also probably not worth the effort on these. We had a test board in the maintenance shop with a variety of PLCs and HMIs on it for the maintenance guys to practice with, so we had them add a section to hold 4 of these just to keep them powered up so the batteries wouldn't drain. It was a pain, but it kept our spares alive until they could be migrated.
 

Similar Topics

I have an opportunity to get some more experience replacing an old Panelview 300 Micro. I'd like to hear any advice you have about it. I suspect...
Replies
12
Views
3,295
I lost the manual for this machine built in 2003 and need to put it back together. I have the Micrologix 1200 and PanelView 300 Micro programs...
Replies
4
Views
1,773
I am tying to download application software to a fresh out of the box PV 300 Micro. The first hitch is a prompt that I am running v4.1xx RSLinx...
Replies
2
Views
1,144
I went on a service call yesterday for a Micrologix 1500. An output wasn't activating and they wanted to know what was hanging it up. It was a...
Replies
10
Views
2,808
I have a Panelview 300 Micro CAT 2711-M3A19L1 Ser A Rev C It gets an error during the startup testing "ERROR! 32" which looks like the Real Time...
Replies
0
Views
1,107
Back
Top Bottom