Can someone tell me if a panelview 600 with ethernet port can be connected directly to a mirologix 1100 plc, and if so, how do you set up the communications.
I would assume that you would have to use a cross-over ethernet cable, if you are not connecting the PV and PLC through an ethernet switch.
Even though you don't have actually one try the NET-ENI communication option. Also make sure to use the crossover cable as smohamed suggested.
Since it is a MicroLogix 1100, a NET-ENI is not needed. Use a crossover ethernet cable to directly connect the PanelView Plus to the 1100, or you can use a network switch to give you an additional port for programming both units.
Another vote for the above set up.
Done it many many times (even with cheap switches), no issues.
Just be aware you may have to adjust CIP settings if you experience "on line edit failures" and such.
There's a few KB notes on how to deal with it.
I suggest using a 4 port ethernet switch and standard cables. This way you have a place to plug in your PC and can troubleshoot both the display and PLC at the same time.
Hi all! I'm trying to restart an HMI which originally showed the message 3a Stuck Touch. I cleaned the HMI, then rebooted it, it now show a...
6,361
How does one get past the password requirement to access the setup (configuration) screen when the user name and password are lost/not known...
2,746
These are discontinued I just found out!!! This pretty much mean the module's toast?
43,138
First time poster. I'm working on getting a Panelview 600 2711-B6C5 to communicate to a 1768-L43 controller through the RS-232 port using a...
3,255
I am trying to go to a 504 CPU. and on my hmi I am getting a 9028 error. can someone explain what they mean by change reference?
229