PanelView and PLCs inputs
HiPo
Aug 2015
Aarhus
Hello,
I am working with a PLC MicroLogic 1500.
I used a mechanical switch (ON/OFF) to start/stop measurements by using Input I:0/0. It works fine.
Now I am using a C300 PanelView and will replace that switch with Function keys:
F2 = start measurements and F3 = stop measurements
Both F2 and F3 are Maintained Push buttons.
Tags: InputA: Boolean, address: I:0/0
Connections: Write Tag: Input A and Indicator Tag: InputA
How can I set 1 to I:0/0 by pressing F2 and set 0 to I:0/0 by pressing F3?
Best Regards
I don't believe you can. While your PanelView may be able to write to that bit, the normal I/O service will quickly overwrite it with the status of the input terminal.
Better to have the PanelView write to a B3 bit and put an XIC instruction addressed to that bit in parallel with the current XIC usage of I:0/0.
What I do in this situation is have the HMI set 2 bits - 1 to bypass the input switch & the other to disable the input switch. You will have to change the HMI PB's to Momentary Set type, or modify the below ladder to compensate for maintained bits.
I was looking for reference, and found this thread http://www.plctalk.net/qanda/showthread.php?t=117141&highlight=multiple+plc+panelview about...
3,004
A while back I submitted the following post: I have an application with two PanelView Plus 7 devices with each one talking to its own PLC. The...
22
12,301
Hey guys, there is a long time that I just read posts here and never write, so it is the time now for that! The company I work for have around 52...
2,258
I have a question about using 1 panelview with 2 PLCs. First my setup: PLC1=SLC 5/05 IP address 192.168.2.100 PanelView= IP address...
3,326
99
