davidl Lifetime Supporting Member D Join Date Aug 2008 Location bristol Posts 6 Jan 27, 2013 #1 i can see the panelview(pv600-2711-b6c2) USING A 1747-UIC CABLE IN RS WHO. dry to down load the program but panelview 32 cannot see the terminal.
i can see the panelview(pv600-2711-b6c2) USING A 1747-UIC CABLE IN RS WHO. dry to down load the program but panelview 32 cannot see the terminal.
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Jan 27, 2013 #2 When you click on download, try selecting "RSLinx Network" transfer type then select the PV in the RSWho window-then click Ok. see picture. Remember "Download" is transferring the PB32 program to the PV. Last edited: Jan 27, 2013
When you click on download, try selecting "RSLinx Network" transfer type then select the PV in the RSWho window-then click Ok. see picture. Remember "Download" is transferring the PB32 program to the PV.
davidl Lifetime Supporting Member OP D Join Date Aug 2008 Location bristol Posts 6 Jan 27, 2013 #3 That worked. it looks like i just did not identify the terminal. THANKS
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Jan 27, 2013 #4 davidl said: That worked. it looks like i just did not identify the terminal. THANKS Click to expand... You're welcome
davidl said: That worked. it looks like i just did not identify the terminal. THANKS Click to expand... You're welcome