panelview display lags PLC execution
realolman
Mar 2009
here
584
I know that the display does not refresh as fast as the PLC executes , but I have a Compact Logix L16ER and a PanelViewPlus 600 , and it seems to me that the display is particularly slow and behind the PLC execution
... I would like to let the user know that the program is doing something when he hits a button, but it's usually long over before the display updates... I would say 3 -4 seconds
Is there any setting to speed it up
thank you
In FactoryTalk View ME, the update rate of each Display is configured individually.
The default is 1 second, which can look more like two seconds depending on when in the 1 second interval your actual event happens.
I usually set up my FactoryTalk View ME screens for 250 millisecond updates unless they are a slow trend.
So this would be in the properties or something similar of each "screen" or where do you set this? FT ME
thank you
Right Click in a blank area on the screen you want to change and a window should pop-up and then select Display Setting. It should be located in the lower left-hand corner.
HTH
Hello brothers We are contacting you because an error like [display change is currently controlled remotely] occurred while using the equipment we...
223
I'm working on a system with three Panelview 7's connected in a DLR. The system started having miscellaneous DLR faults and they were supposedly...
491
I'd like to have a display in my view studio runtime show the current ip address of the panelview. I know how to fetch the plc ip address but I...
1,269
Hello friends, Is there a way to pop up a display on PV HMI, using the status of a plc tag value, other than using a goto push button? Thanks
1,741
First time using a panelview. I have all of my alarms mapped to bits of dints. How do I get the alarm panel to popup when an alarm happens...
2,134