"Panelview offline" message on PV300
Deer
Jun 2002
124
Hi all,
Does anyone know,what caused the problem message "Panelview Offline" on the Panelview300 micro (RS232/DF1, 2711-M3A18L1)would be appear on the display PV300 ?
Many thanks
Deer
Very likely it's not plugged into a similarly configured DF1 port on a controller.
Do you have a proper (null-modem, with Tx/Rx swapped) cable connected to the controller ? Is the controller serial port set to the same baud rate and error checking as the PanelView ?
For the panelview to be " online " it needs to be plugged into the PLC and the PLC needs to be powered up. Also, if I am correct the PV300 micro wheather it be DF1 serial 232 or DH 485 they both come only with a 9 pin round plug connection so check if it is serial or DH 485 you can check this by entering the the communications menu or check the product number against the manual provided.
Regards
Peter
hi guys, im new on programming the panelview (600).I have couple of question. 1st when i lay out the start button on the panelbuilder then...
6,259
96
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
59
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
187
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
89