Panelview Plus 1250
lifetech
Dec 2012
Arcade, NY
39
Hi All
I am trying to get the correct date and time set in my PV+1250. I have read the manual and nothing seems to work. I would like to know if anyone has the correct instructions on how to set the date and time. Also, I would like to eventually set up all the PV+'s to get the time off of one of the slc 500's on the network. I would apprieciate any help.
Are you using the Configuration Mode menus, or the Global Connections feature ?
Since your goal is to get all the PV+ terminals reading the time from an SLC controller, you should work on the Global Object connections.
It's the "Remote Date/Time" connections that allow the PanelView Plus to read the date and time from a controller. Do not attempt to use both the "Date/Time" and the "Remote Date/Time" connections.
The non-obvious thing is that the PanelView applies the values in the Remote Year/Month/Day/Hour/Minute/Second connections only when the tag associated with "Remote Date and Time" goes from false to true. It reads all of those tags at the "Maximum Update Rate", which I usually leave at 1 second.
Hey guys, I'm at a bit of a loss with a problem I'm having with some PVP 1250s and hoping for some advice. In firmware and application version...
302
is it possible to comunicate a powerflex 753 (ccw) using ethernet 20-750-ENETR card to a panelview plus 6 1250 (factorytalk view studio me)...
1,504
Hello, I recently installed an **** Flexy 201 so we could monitor our PLCs (one SLC 500 and one Control Logix) remotely under a VPN. One of the...
2,374
Hi, I have a customer that has an intermittant issue with a PV+ (2711P-T12C6D1) and they would like to replace the PV+ with the latest PV+7...
3,001
I have these PLC and HMI and want to communicate them. I made a program in RSLogix5000 and FactoryTalkViewStudio, tried them out with FT station...
4,426