PanelView Plus Micrologix 1400 help please
IanHough
Jun 2016
Vancouver
Hi there,
I seem to be having some issues interfacing a Mircologix 1400 and a Panelview plus 1000. All communication is done over ethernet.
ML1400 (1766-L32BWAA) Ser.B FW.15 IP. 192.168.0.2
Pvp1000 Logic Module (2711P-RP2) IP. 192.168.0.100
Terminal (2711P-T10C4D2) Ser.A
I am able to create a simple application in Factory Talk View Studio - Machine Edition and create a runtime 6.0 application. I am able to test the application on the pc, where I can see the bit I have assigned, to the start button, go high and low in the rslogix500 program.
When I go to transfer the application I get an error saying there is an unrecognized device on the network, the ML1400.
Both the Micrologix and the Panelview are present in rslinx enterprise and classic.
I tried downloading the application without the ml1400 on the network and the application appeared, but obviously there was an error when there was no response from the plc.
I feel like im close im just not sure where to go from here.
Thanks for any help!
-Ian
What does your Rslinx Enterprise config look like in ME? Can you take a screenshot of both the local design and runtime tabs?
Hi Dravik,
I need to figure out how to get the screenshot posted, I spend more time reading forums than I do posting.
I can tell you I selected the ML1400 and added it to the device shortcuts, and applied the changes. From there I clicked 'copy from design to runtime'
Each tab, Design(local) and Runtime(Target), currently looks the same.
Ill work on getting those images.
Thank you for the reply
85
Hi PLC People, I get the following error when trying to compile a Panelview Plus 7 Standard program Using View Studio V10.0 Device Shortcut is...
4,867
Hello, I am currently installing a PLC control panel and due to space constraints, we will need to install the Panelview 600 HMI separate...
3,378
HI, I would like to link (via ethernet) a PV+ to a micrologix 1100 already on an ethernet IP adresse (they are not in the same panel or location...
1,892
Hello all, I am having an issue at a clients site whereby a loss of comms between a PV400 and a micrologix 1200 has occurred. The PV is connected...
4,044