I've done a factory reset on a PV 7 Plus terminal, set the IP address and cycled power.

I can now ping the PV and can see it on RS Linx but its not appearing when browsing using FT Linx and consequently I can't download the application.

The ME station firmware is 10.0.9, FTView Studio is rev 12 and I'm using Ethernet/IP to communicate.

What have I missed??
 
If you can see it in RSLinx that suggests the problem is not with the PVP terminal.

Try deleting and recreating your driver in FT Linx; I've recently had occasional problems with FT Linx not wanting to detect things and that usually resolved it.
 
I will state the obvious first to get it out of the way...

Right-click on the Ethernet driver and if there is an option that says, "Start Browsing", select it. If it says, "Stop Browsing", do not select it, you are good. I have had cases where I just could not get it to see my device no matter what I did. When that happened, I manually added the device in FT Linx.

If you right-click on the Ethernet driver and select Add Device you will find the PV+ 7 near the bottom of the EtherNet/IP Devices category. Adding it manually seemed to sort of wake-up FT Linx to the device and I was able to talk with it. Worth a try.

OG
 
Many thanks for your prompt responses.

In the end I cycled power to the Stratix switch and that sorted it!?
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
87
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
56
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
86
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
Replies
0
Views
93
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
136
Back
Top Bottom