PanelView Plus screen problem
pimpim32
Mar 2003
123
Hi everybody,
I have a PV+600 monochrome touchscreen at 110V supply.
Worked fine at testing but now at machine startup at client site, when I turn power off for the machine drive he decided to show only half screen.
The buttons still working if you know where they are, but no info.
I will exchange it under warranty but I was wondering if it happened before to anybody and if is any solution availible.
Calling AB they said to try updating firmware. Updated to 4.00.11 no luck.
Thanks for any hint.
Marian
So nobody came across this problem?
As more info in same circuit with the PV+ I have 1 brake(~1A), main contactor(~.75A), a bunch of other relays, all in all never goes over 3.5A, the transformer being .75KVA 480-115.
As I said I will replace it tomorrow however it bugs me the ideea not to know why it happened.
As I know AB PV's are pretty solid, aren't they?
At least they should be for how much they cost.
Hi
I never had the problem you have,but I did have a new one
out off the box fail to power up.I also had one fail 1 week or so
after I had installed it.I sent both back to rockwell and I did not
find out what went wrong with them.They did replace them both and
I did not ask after I sent them back to see what was wrong.
I know I should have but I forget about it.
Donnchadh
I have 2 PV Plus 7 screens used in the same system that both have touch screens that can be challenging to activate after they haven't been...
577
Every time I power this unit up it loses its IP address and goes to DHCP . When I goto the config the IP address is 0.0.0.0
737
Any good idea how to dim the display on a panelview plus performance serie b, at idel. Screen saver is not supported yet I have don it in global...
2,234
New PanelView Plus 7 Performance Series B P2711p-t10c22d9p out of the box I went through the touch calibration screen and then to the "Welcome to...
4,901
I am having an issue where the alarm history on the HMI is zoomed way in. It is as if even though my font size is set to 6pt in factory talk ME...
2,783