Parameter download to siemens DB
maico
Jun 2012
Belfast
27
If a parameter is loaded by the HMI to say DB83.DBW132 and I go to the DB and find this parameter but when I use goto location there is no location shown so where is this parameter used in the program?
The parameter may not be used as a Word or integer, but instead as a set of bits (typical for the alarm configuration, for example).
On the goto pop-up window, there will be a tick box just above the buttons mentioning something like other places used or different data types... tick that and see if it pops up.
Another possibility, which will be a pain to figure out, is if someone feeds the number 83 to an FC or FB to create a pointer and use that DB via indirect addressing. If that's the case then you'll have to check a bit more stuff than normal.
right
DB83.dbw132 is the same as DB83.dbx132.0 to 133.7
It can also be DB83.dbb132 to dbb133
and DB83.dbd132 (including all of 132-133-134-135)
This reminds me of a program I came across that had hundreds of DB's but in the code only one DB was used.
The entire functionality was done via pointers and that would be configured by writing the correct values in the correct DB's. It was some of the most intricate programming I've ever seen... and you could configure the whole thing by reading a 200 page manual and writing the correct numbers to the correct fields in the DB's.
Hello, I am trying to get all of the parameters backed up for our 12 Danfoss VLT 5000 drives. We are upgrading to FC-302 drives and I would like...
7,588
i am having some problem with control techniques make commander sk drive. i wants to download the application drive parameter and the SM...
2,408
Is it possible to program the parameters of an Danfoss VLT2800 over a profibus network? And if so how can this be done?
6,718
This is probably aimed at Jesper. I have a S7 300 with a Simocode pro c motor controller connected on profibus DP. How can I detect if a new...
12,188
298