PF753 Profibus 20-COMM-P help needed.
Ken Moore
Lifetime Supporting Member
Join Date
May 2004
Location
North, West, South Carolina
Posts
3,475
Ok,
We have a couple of hundred PF753's with 20-COMM-P cards installed.
I recently had one fail, and it would not communicate over the replacement. Both have same Firmware revision. Only difference is one dated 2012 and one 2018.
What am I missing. They are marked E for existing and N for new. Short term fix was to pull one from a spare drive.
Solution found:
It seems that on some but not all new 20-COMM-P cards, once the card is installed and the drive is powered up. From the HIM, go to the COMM card, parameter 8, and reset the module. Then it works.
As we say in the Siemens world, another undocumented feature.
Solution found:
But those interface cards are made by AB, so how is it Siemens fault?
Excuse me if I am putting words in OP's mouth, but I don't think they were blaming Siemens, rather they were making an analogy by saying that AB can be as incompetent as Siemens in the "that's not a bug, that's a feature" department.
Similar Topics
Dear Sir, I have a healthy profibus communication between SIEMENS PLC S7 400 and Allen Bradley drive PF700 using 20-comm-p profibus dp module...
Replies
3
Views
2,822
Sigh, DeviceNet noob... I have a 1756-L55, with a DeviceNet module, and 10 PF700 all commanded with DeviceNet. One of the PF700's blew up...
Replies
3
Views
133
Hello all, Who have links for documentation,- how to connect Allen Bradley 3 phases VFD PF753 in test purposes using only 230V. Approximate...
Replies
3
Views
1,559
Hey everyone, Running into a snag while commissioning some PF753 drives onsite. We have a ControlLogix L71 processor with an EN2TR card in the...
Replies
8
Views
1,981
I have a strange one for you guys. I have a PF753 with an encoder card, driving a Baldor variable speed motor with an encoder. It started flaking...
Replies
0
Views
1,617
Back
Top Bottom