PID GAINS IN SIEMENS 300 series
ravilal
Feb 2006
karachi
WHY THE PID(PROPORTIONAL,INTEGRAL AND DERIVATIVE) HAS SAME GAIN VALUE IN SIEMENS 300 SERIES.HOW CAN I INSERT DIFFERENT GAIN VALUE,i.e different proportional gain,different integral gain, and different derivative gain?
Hello ravilal;
I will presume you are using FB41 in Step 7; the flow diagram for this function is illustrated below:
The input and output symbols of this diagram represent the parameters of FB41. You will find Gain, Ti and Td on the diagram; these represent Proportional gain, Reset time and Derivative time; whatever value you enter here (a REAL numerical value, or preferably a REAL variable from your program) will be the different gains of your controller. Notice that the BOOL values P_Sel, I_Sel and D_Sel must be ON in order to select the gains (these BOOL switches sallow you to select a P-only controller, a PI controlle, a PID controller...).
Hope this helps,
Daniel Chartier
Just be sure to place your FB41 block in OB35, it will save you from frustration I had when tried to tune PID controller for the first time. Otherwise, time constants Ti and Td won't mean anything.
Factors And Offsets In Pid In Step 7
Thanks for answering.Can you tell me when and where do we use
PV_FAC and PV_OFF used in PV NORM block in PID loop in FB41 of siemsns S7? and similarly LMN_FAC and
LMN_OFF in LMN NORM block.What are practical applications of using
these factors and offsets in these blocks.what are their uses?what are they for?
Do the gains in the RSL5000 PID instruction work on values in percent or in engineering units? Trying to help a colleague in the field tune a...
1,533
Hello I'm working on a winder at the minute. I'm a winder virgin. I'm controlling the winder's speed based on the line speed/diameter trimmed with...
2,049
There are many applications that are non-linear where one set of PID gains don't do a good job of a wide range of operation. There are...
19
7,129
I've got a loop that is extreemly well tuned for a CLX PIDE. I also have a SLC5/05 that is controlling an identical piece of equipment at a...
6,730
86