WHY THE PID(PROPORTIONAL,INTEGRAL AND DERIVATIVE) HAS SAME GAIN VALUE IN SIEMENS 300 SERIES.HOW CAN I INSERT DIFFERENT GAIN VALUE,i.e different proportional gain,different integral gain, and different derivative gain?
I will presume you are using FB41 in Step 7; the flow diagram for this function is illustrated below:
The input and output symbols of this diagram represent the parameters of FB41. You will find Gain, Ti and Td on the diagram; these represent Proportional gain, Reset time and Derivative time; whatever value you enter here (a REAL numerical value, or preferably a REAL variable from your program) will be the different gains of your controller. Notice that the BOOL values P_Sel, I_Sel and D_Sel must be ON in order to select the gains (these BOOL switches sallow you to select a P-only controller, a PI controlle, a PID controller...).
Just be sure to place your FB41 block in OB35, it will save you from frustration I had when tried to tune PID controller for the first time. Otherwise, time constants Ti and Td won't mean anything.
Thanks for answering.Can you tell me when and where do we use
PV_FAC and PV_OFF used in PV NORM block in PID loop in FB41 of siemsns S7? and similarly LMN_FAC and
LMN_OFF in LMN NORM block.What are practical applications of using
these factors and offsets in these blocks.what are their uses?what are they for?