I've been reading through many of the posts on this Forum, lucky i found similar problem in-regard to PID Loop and concerning PID process control in RSLogix 500. I have developed a programmed the control incorporating all that I've gathered ideas on this site, however I am not getting the PID Loop to fully functional and control my intended process and wanted to ask a help from you and to all great mentors here in this forum, Did i something miss on my program?
Thanks a lot and for your patience..
  • wATER FLOW.pdf
A little more info about the above would help someone help you.
From what you have posted your PID instruction should be on a unconditional rung.( remove the GEQ amd LIM). If you want to check the process variable for a valid value do it on a rung above the PID.
It also would be best to post the whole program, it's .RSS file ( zip it first)
Hi, Thanks a lot for the reply,
I tried to removed the GEQ and LIM, but still the same, Scaled Error of PID still 0.
Please see the attach file of Plctalk.zip..Please do changes if their something that i missed.
Thanks a lot in advance.
your PV is coming from N7:100 ... why? ... that appears to be a static number – NOT a number from an analog input ... (did you just type this number in for testing?) ...
your PID has a setpoint of 600 ... the PID sees your PV as a scaled value of 983 ...
basic answer:
since your PV is already above the SP, then the PID is trying to DECREASE the output (the CV) ... currently it has the output turned completely off ...
suggestion: type in a series of smaller and smaller numbers at N7:100 ... once the PV goes below the SP, then you will probably see some output action from your PID ...
Mickey is right – in RSLogix500 systems your PID must be on an UNCONDITIONAL rung in order to give you good results ...
DISCLAIMER: swamped with work right now – this is just a quick glance ... I'll write more later if possible ...
basic answer:
Yup, N7:100 is link in the HMI so that i can easily manipulate the simulation analog input in the HMI.
I tried SP greater than PV based on the E=SP-PV, but still the same no output even the Scaled error still zero, did i missed something on the PID?
and also i tried to removed the GEQ and LIM but still the same..maybe there something that i missed.
Thanks a lot.
Post your corrected program, the one the above screen shot is from.
Save the program while it's in the run mode.
Hello all, I have been ask to convert a program from RSLogix500 to TIA V15.1 (S7-1500). The program uses a few PID loops. From RS500 the...
1,322
Hi guys, im a sparky that is slowly getting into the PLC Programming side of things rather than just troubleshooting. I have been asked to...
1,993
Can anyone help me to provide an explanation of the TUNING OF PID FOR AB SLC500
8,847
Hi I need help with tunning pid block for Allen Bradley’s PLC SLC500 and processor 5/03. Only for test how to use this instruction I download a...
4,599
I have read some article here about bipolar method for PID that I have to read it but I could not find any manual for this one. Could some one can...
3,078