Hello,
I have 2 PIDE's controlling the same valve. One, opens the valve to a setpoint pressure. it switches to the other PIDE to close the valve if motor goes in overcurrent. I have both PIDE's going into a SEL that picks which output to use. Here's the question: i am using valve feedback position into CVPrevious for a bumpless transfer feature. if I enable a different PID with the actual valve position loaded into CVPrevious, is that where the CV will start from? in otherwards, i don't want one calculating while the other is controlling-Or even if it does- i want it to start at the present valve position. thoughts??
Also, if the operator is to have manual control over the valve, it would seem you'd program a third input to the ESEL; this would be the 'manual output value'. It would seem InsUsed input parameter would remain 2 (In1 from pressure PIDE, In2 from overcurrent PIDE). You'd have to play with Selectormode and other parameters to get nice bumpless transfer from auto to manual and back again, as well as coerce the 'manual output value' to Out output parameter when the loop is in auto (for bumpless auto-to-manual bumpless transfer).
See http://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1756-rm006_-en-p.pdf and forgive me any imprecise use of terminology in the above description.
I am working on a large migration of the standard PID instruction to the PlantPAx P_PIDE. Has anyone done a migration like this before and have a...
83
Hello all, we have an homogenizing oven with three zones, 2 burners in each zone, a soak (smaller) and a main (large). during ramp to the air...
194
Greetings ... someone sent me a request for some student handsouts that I developed ... turns out that I had this hosted on my business website...
152
Have a logix controller and I'm using the PIDE block for the autotuner. I've got the hang of doing it for direct control things like pressure...
21
1,818
Studio 5000 version 34. Have error on PIDE CVFaulted (Status1.2), Control variable (CV) health bad. No more information online or in...
981