Plc 5/60 RIO to a 20-Comm-R
Darkzadow
Nov 2011
Phily
94
I have a PLC5/60 with 4 DH+/RIO connectors and a 20-comm-r module on a Powerflex DC drive. I have the PLC channel configured as RIO scanner. For the rack settings in the plc I have rack 4, group 0, size 1/2, Inhibit 0, range 040-043, 57.6k baud. On the 20-Comm-r i have rack 4, group 0, size 1/2, 57.6k baud.
On the comm r the Port is solid green(connected to Drive), Mod light is flashing green (no comm detected) and the net A is dark (The adapter is not powered
or is not connected properly to the Remote I/O network). I have the adapter powered and have tried both blue and clear wire configurations, with and without terminating resistor.
What am I doing wrong for the connection or is 20-comm-r on powerflex dc, and PLC 5/60 with the built in 4 dh+/rio channels not a possible configuration? (then im boned.....boned bad)
Just an update I used the manual switch settings and removed the terminating resistor(was last drive on that RIO channel but whateves) and got one of them working 2 more that I am playing with ( they are the last 2 on their channel)
Normally you don't use a resistor with a 20-COMM-R as it has one built into the module. You turn it on or off with the dip switch setting. If you had a physical resistor in place also and this enabled that could be part of your original issue.
Ok that explains that one, Thank you. I tried that with the other pair but no luck. Still digging through cabling and settings
Greetings all first wanted to say thanks for all the great info as I have been looking here a lot trying to figure out my issue, but having said...
4,781
I am trying to send some datas from PLC-5 to control logix plc through 1756-DHRIO. When I go online to PLC-5, Message instruction gives error &...
3,375
My PLC is a TRIO Flex 6 Nano and my HMI is a LT4301 Proface. I have a sensor wired up to the hmi and its working correctly. I want to have the HMI...
3,590
My customer has a PLC-5/80 with 20+ RIO racks. They've asked me to remove one of the racks without shutting the system down. Can I set the...
3,995
Hi, I am trying to learn how to use my encoder with my PLC. I recently got a high-speed counter module (H0-CTRIO2) for my DirectLogic05 PLC. I...
2,215