This will be one of those "I'm not a PLC guy, but I'm helping them troubleshoot" questions. I'm on the computers / network side.
We have a PLC-5/80E that has had some off and on issues with it suddenly not responding to the RSSQL. Almost always we can reset the network port on the Cisco switch and communications resumes.
One of our Cisco guys had said that the port went down due to the connection flapping.
We have had our wiring contractor previously run brand new network cable in and we moved to another port on the switch and that seemed fine for a few months but then the problems returned a couple of weeks ago.
I went ahead and ordered a new 10BaseT transceiver for the PLC just to rule that out.
Previously a former employee had locked that port to 10Mbps/Half Duplex several years ago because "the PLC couldn't keep up" But another person had said that it was set that way because the Transceiver didn't support full duplex. Well this new one does so we set the port on the switch to 10/Full and set the transceiver to Full as well.
It's been running fine tonight (but then again it tends to work fine for hours or days before it dies out again)
I've been keeping an eye on the General Ethernet Counters and this particular PLC seems to be getting lots and lots of Carrier Sense Errors. Thousands and suddenly jump to 4 billion and then reset.
Unfortunately I didn' t notice those errors were there before or not.
Here's a snapshot of what I just got:
Do they need to have their ethernet duplex configured separately from the transceiver? I can pull up the PLC in RSLinx Classic on the RSSQL but I don't see any options for ethernet settings.
The cabling going to it is only 6 months old so I don't think it should have gone bad again (I plan on doing a continuity test on it either way whenever production isn't running)
In a nearby cabinet we have a 5/40E and it has zero carrier sense errors, but still gets a lot of packet storms.
The 5/80E is sort of the main PLC for that line from what I understand. It talks to the RSView computer, RSSQL, the 5/40E and another PLC cabinet with a CompactLogix in it that deals with some fan control stuff in the area.
Here's some information from the Module Information page as well (if that helps any)
We have a PLC-5/80E that has had some off and on issues with it suddenly not responding to the RSSQL. Almost always we can reset the network port on the Cisco switch and communications resumes.
One of our Cisco guys had said that the port went down due to the connection flapping.
We have had our wiring contractor previously run brand new network cable in and we moved to another port on the switch and that seemed fine for a few months but then the problems returned a couple of weeks ago.
I went ahead and ordered a new 10BaseT transceiver for the PLC just to rule that out.
Previously a former employee had locked that port to 10Mbps/Half Duplex several years ago because "the PLC couldn't keep up" But another person had said that it was set that way because the Transceiver didn't support full duplex. Well this new one does so we set the port on the switch to 10/Full and set the transceiver to Full as well.
It's been running fine tonight (but then again it tends to work fine for hours or days before it dies out again)
I've been keeping an eye on the General Ethernet Counters and this particular PLC seems to be getting lots and lots of Carrier Sense Errors. Thousands and suddenly jump to 4 billion and then reset.
Unfortunately I didn' t notice those errors were there before or not.
Here's a snapshot of what I just got:
Code:
Commands Sent 15846
Replies Sent 811082
Commands Received 811082
Replies Received 15768
Replies Sent With Error 0
Replies Received With Error 0
Replies Timed Out 81
In Octets 1265264
Out Octets 981409
In Packets 15449
Out Packets 10550
Alignment Errors 0
FCS Errors 0
Carrier Sense Errors 10541
Excessive Collisions 0
Excessive Deferrals 0
MAC Receive Errors 0
MAC Transmit Errors 17
Single Collisions 0
Multiple Collisions 0
Deferred Transmissions 22
Late Collisions 0
Packet Storms 18041
Do they need to have their ethernet duplex configured separately from the transceiver? I can pull up the PLC in RSLinx Classic on the RSSQL but I don't see any options for ethernet settings.
The cabling going to it is only 6 months old so I don't think it should have gone bad again (I plan on doing a continuity test on it either way whenever production isn't running)
In a nearby cabinet we have a 5/40E and it has zero carrier sense errors, but still gets a lot of packet storms.
The 5/80E is sort of the main PLC for that line from what I understand. It talks to the RSView computer, RSSQL, the 5/40E and another PLC cabinet with a CompactLogix in it that deals with some fan control stuff in the area.
Here's some information from the Module Information page as well (if that helps any)
Code:
Processor: PLC-5/80E
Series/Revision: E/K.3
RAM Status: Good
Processor Mode: Remote Run
Major Faults: 00000000 00000000
Minor Faults 1: 00000000 00000010
Minor Faults 2: 00000000 00000000
Program Name: LINE_1
Firmware Identification: 1785_np580e 2.64 16-Jan-07