I'm running into an issue migrating a PLC-5 using the newer Logix Designer Export when opening a saved .ACD from RSLogix-5.
It has multiple RIO chasses, to CLX. No matter which option I select after opening the saved .ACD (Keep Existing I/O vs. Update All I/O), it will only fill one chassis worth of I/O. In other words, 29 total modules, but it only creates 16.
So far, the only thing I've found to do is create placeholder tags for all 29 modules, properly add the I/O modules in the respective chassis, and then do a find/replace for the placeholder tags.
Has anyone found a better way to handle this?