PLC 5 PID question - MAX Scaled Input
skyfox
Nov 2006
CA
279
I am trying to figure out how to calculate the 'UNSCALED" Setpoint value based on operator entered PID setpoint. Not sure I have all the terminology correct. Read thru the PID instructions but still a bit confused.
Input to the PID Process Varibale (PV) is 0-4095 (Instrument range = 0 to 150psi)
What should I used for " MAX Scaled INPUT" Parameter? Better yet, where do I find what I need to enter in to this register? In other words, what determines this MAX scaled input value?
What is the unscaled Setpoint value? is this an user entered parameter or PID instruction generated value?
Thanks.
The actual math depends on your input card raw signals.
Use the whole range of 0-4095 (unless you wish to use and have a CPU that supports a floating point PID).
Figure out the slope and offset to get that from your input card values, and apply the math just before you execute the PID.
The intstruction set reference will give you the mechanics, search for post by Ron Beaufort with BOTH PLC5, and PID for laymans terms applications and fantastic explanations.
I saw in a 24 V solenoid valve which has 3 wires (2 reds, 1 green); so 1 red is 24V power, another red is .... a common ??? or the green is the...
4,276
Hi all, I've been a long time follower of this forum, but this is my first time posting. I'm dealing with a PLC5/20 and was hoping to get better...
2,688
Would using a PLC PID to control a motor of a loss in weight device where the motor is controlled through a Modbus or ethernet connection be a...
3,232
I am doing a wire spooling application using an Automation Direct D-260 cpu, F2-8AD4DA-2 16 bit 8 ch in / 12 bit 4 ch out 0-10 vdc board. The...
5,409
Hi all, Got a quick question. Might be stupid and stright forward, but have to ask it. I have a loop being excecuted in a PLC5 PID loop, that...
5,121