PLC Modicon EtherNet connection
yourlove761
May 2012
Hobart
Good-day everyone.
I am doing a project with Modicon, however I am currently stuck at controlling PLC via EtherNet o_O.
An example that basically demonstrate my problem:
PLC1 control LED1 - controlled by a button
PLC2 control LED2 - always ON
When LED1 ON, LED2 goes OFF automatically.
Both PLCs have IP@ and connected to an EtherNet network.
My goal is nearly achieved, any help is appreciated.
Hi there,
Firstly, we need to know what PLC exactly (not just Modicon, that could be anything from the late 80's through to a modern processor now, hundreds of models) and what software you're using to program it - Unity Pro maybe? Or is it a more basic processor?
Then we can help.
Sorry, I forgot to include the detail.
Both PLC are Modicon Premium TSX P573634
The software I use is Unity Pro.
Thanks for your quick reply Saffa
The easiest way is to use io scanning (search in the help for a full description). Basically you create a table in the comms section (it is a tab on the ethernet setup) and the plc does the rest. Just make sure you have located the tags (set them to an MW address) in the source plc.
We use the method Geoff has described, however it's between remote I/O racks and a main PLC, not PLC to PLC so I can't comment on that. There are messaging FBs which can be used to read / write %MW values, but I've never used them so other than saying "look in the help file", I can't help you much there. There are some reasonably straight forward examples, but as with most Schneider help files, they're preeeetty basic.
There is also another method called Global Data or something like that. Basically you can set up a small set of "shared" memory which all controllers will broadcast to the network. It does require your network be able to support multicast though. Again... haven't used it, just read about it!
If you've got the controllers up and running and its not a production environment, i'd just try setting up one of the examples in the Unity Pro help file. Do a search for READ_VAR and look in the communications FBs and Premium/Atrium, Ethernet communication.
Thanks both Geoffc and Saffa very much. I can solve my problem at the moment by using the io scanning service which Geoffc recommended.
Now I am trying to use other two methods: Global Data & Messaging so that I can compare which one is the best method for coding.
Nice to meet you two.
Saffa - IO scanning can be used for plc to plc comms. Just finished a project linking 4 plc together using this method
We have a Modicon PLC that is connected to the Ethernet Network and we have three CompactLogix PLC's connected on this network as well.. I need to...
7,087
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
318
Hey all, I do not have the original source code of a Modicon M172 PLC (HVAC PLC). I want to modify some of the code but read you cant upload...
398
HELLO MY FRİENDS ı have problem. ı tought you can solved thıs problem for me. First of all When I checked all the cable connections of the...
417
We've got this old Modicon PLC on a Mobile Skid that has developed "Comm" errors that cannot be cleared (tried moving cables, connectors etc.)...
1,100