Modicon PLC Ethernet IP To CompactLogix Communications

plcengineer

Member
Join Date
Jan 2004
Location
USA
Posts
176
We have a Modicon PLC that is connected to the Ethernet Network and we have three CompactLogix PLC's connected on this network as well.. I need to message between the two and was wandering if anyone had done this before??? I should be able to use Message statements from the Compactlogix etc..

Thanks,
 
I believe Modicon and AB speak different dialects of Ethernet. I have always had to install and set up a Prosoft module in the AB rack such as the MVI69-MNET card. This will speak to the Modbus controller in Modbus TCP/IP.
 
Probably wont help you at this stage, but worth passing on. The new Modicon plcs will have Ethernet/IP built in. The Quantum ethernet/IP module is already available, so this may help if using Quantums
 
This modicon PLC is connected to the Ethernet IP network as well as the CompactLogix.. So, can I do messaging without additional hardware?
 
This modicon PLC is connected to the Ethernet IP network as well as the CompactLogix.. So, can I do messaging without additional hardware?

My understanding that the Modicon Ethernet/IP (CIP) capability was not upgradable via firmware, ie you have to get hardware that specifically supports it when it is released. This is based off an offhand comment by a Schneider rep many months ago, so take that with a grain of salt.

If you do not use the Modicon CIP enabled network module, you will need to get a third party module such as the aforementioned Prosoft module which works very well.
 

Similar Topics

Good-day everyone. I am doing a project with Modicon, however I am currently stuck at controlling PLC via EtherNet :banghead:. An example that...
Replies
7
Views
3,317
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
Replies
6
Views
275
Hey all, I do not have the original source code of a Modicon M172 PLC (HVAC PLC). I want to modify some of the code but read you cant upload...
Replies
2
Views
347
HELLO MY FRİENDS ı have problem. ı tought you can solved thıs problem for me. First of all When I checked all the cable connections of the...
Replies
0
Views
404
We've got this old Modicon PLC on a Mobile Skid that has developed "Comm" errors that cannot be cleared (tried moving cables, connectors etc.)...
Replies
2
Views
1,093
Back
Top Bottom