PLC or RTU?
Jan 2013
california
32
Hello, I'm interested in hearing your thoughts on weather to use a PLC or RTU for a water/wastewater Scada System. I'm currently undecided on weather to use Allen Bradley or ScadaPack for our out station controllers. I'm very familiar with Allen Bradley in the manufacturing environment so I'm naturally drawn to there products however not sure if there controllers would be ideal for a Scada system? Some of the things that concern me are power consumption. I've never used ScadaPack before so not sure what the pros and cons are. Majority of our sites have power with the exception of a few solar powered sites. We use IP/Radios. Any thoughts about the subject would be appreciated.
It really depends on several things:
* What you outstations consist of, i.e. are there complex control requirements
* Reliability of communications infrastructure
* bandwidth available from communications infrastructure
Typically I use RTUs for standard, simple applications e.g. 2 pump wastewater pump stations, water reservoir, flowmeter station. For a treatment plant, almost always a PLC. Depending on communications infrastructure available i may still have an RTU on site just to bring back data to the master station.
The reasons I like RTUs for difficult or semi-reliable links is that their communications protocols are simple and bandwidth efficient and i can log compliance data locally in the RTU and pull back to the master when the radio channel isn't busy.
Conversely, RTUs are typically not suitable for complex control.yeah they can probably do most stuff at a pinch, the feature set is not always there, e.g. PID loops, IO scanning, online edits. I'm not familiar with SCADAPack though. I know a contractor who hates PLCs and throws RTUs at everything. His clients are always having issues and don't get good value for money.
I don't think you should limit yourself to one technology. You need to start by understanding what sites you have and their control and IO requirements. Then what features do your operators need on site? If they need local HMIs, will that work with your RTUs? Etc.
Then how your communications network needs to look to reliably bring data back to your base station. Then i like to consider what happens if you lose Comms. Can your pump stations still run without knowing a level in a tank? Have you implemented an interlock that will cause a sewer station to overflow if there's no permissive signal from a downstream station? Those sorts of issues need to be addressed as well.
I've only ever had the pleasure of implementing a system from scratch once. We went with a mix of RTUs and PLCs as we had wide geographical area and needed to use 3 different communications methods! PLCs at the larger plants and radio and cellular RTUs for the rest.
I've seen others with just RTUs... and there are definitely problems. Can sometimes be the wrong tool for the job.
I look after one 3 station AB PLC system that uses the DF1 radio option which has had no issues in nearly 10 years despite next to no maintenance. But i don't know how well that scales to say,100 sites.
Hope that waffle is of some assistance!
Also what does the weather have to do with it? Will everything be mounted outside?
Whether the weather be fine
Or whether the weather be not,
Whether the weather be cold
Or whether the weather be hot,
We'll weather the weather
Whatever the weather,
Whether we like it or not.
Hey everyone, I am seeking assistance on finding and solving potential cause of a Modbus RTU issue, from a Micro820 PLC. We are unable to...
1,329
Hello Guys, I have a packaging machine in the company that I work for that have 8 Omron VFDs (3G3MV ) that are controlled via Modbus with CJ1M...
663
Hello everyone! Posting from Argentina as I don't know what else to do. For a bit of context, I am using an Allen-Bradley Micro850 PLC and five...
10,509
Hi, I'm trying to setup a ControlWave Micro (CWu) to read tags from an Allen Bradley ControlLogix PLC (L-61 CPU) using CIP comms. The CWu needs...
2,232
Hi all, Has anyone dealt with Modbus RTU communication using SE`s Machine Expert? I have got the modbus tcp working, but not used the serial...
1,215