PLC output fused for Isolating relay
sportster
Mar 2005
WI
113
Question... for those of you that use isolating relays on the outputs of your PLC cards; do you still fuse the outputs of the card? See pdf for example with outputs fused. It seems overkill to me to fuse an output just to fire a little relay, but part of me just can't leave those outputs un-fused. I need to use the isolating relays to drive loads that are higher than the PLC outputs will handle.
Thanks,
Patrick
If I have outputs turning on an isolating relay, I rarely fuse the outputs, and instead have a fuse on the supply voltage to the relay output.
Or if it's a small enough power supply, I just put a fuse on the output of the power supply and let that take care of the rest of the machine. I have lots of machines that only have a 50W 24VDC power supply. They have a 2 amp fuse on the power supply, and that's it.
Thanks,
Patrick
Yes I do. I don't want any one output taking out all outputs.
I do the same thing. Just one fuse for every relay output card. If it is a regular output card with interface relays mounted in the same cabinet I do the same. If the outputs are connected directly to the equipment or to another cabinet, I usually use a single fuse for every output.
I agree with Mickey. I fuse every output. Just because one of them goes doesn't mean I want to lose the others. Plus, sometimes a shorted solenoid can burn up an output completely. If I have each output fused individually, then chances are I'll only burn up one. This way I can swap it over to another output address and keep on rollin'.
I guess it all depends on the application, but that is how I usually do it.
This is what Siemens is saying about their DC transistor Output cards.
"DC outputs :
Fusing to protect external wiring and DC power source only is acceptable. Transistor outputs will typically not be protected by a fuse unless additional current limiting is included. The transistor bond wires will open faster than a commercial fuse. If short circuits are expected, a 3 ohm resistor in series with each output, or a DC power source that instantly limits maximum current to 8A, will allow an external fuse time to act. External fuse for this case should be 1A or less with an I*I*T rating of 5.5 or less."
Sounds good. I agree with you guys on fusing the all the outputs all the time. But I normally don't have to use isolating relays to switch loads. So that's why I was questioning leaving the fusing out. I think I"ll just go with fusing the whole card and size it accordingly. Thanks, Patrick
I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
120
I have a project to control the speed of motor DC using PWM Output on PLC and when im on working i have a several trouble and of of them is the...
234
Hello, the PLC in question is 1769-L30ER. I have a local 4-20mA Analog Output module (1769-OF4CI), and also a remote ethernet PointIO analog...
402
Hi guys, i have never had to do a PWM Output or input before i have a Device that to dimm the lamp output from the ballast, the ballast has a 24V...
1,064
Hello everyone, I am having issues with an output module connected to my 5069-L306ER PLC. The modules I have connected are a 5069-IA16 in slot 1...
708