PLC output surge suppressor
pg207
Apr 2014
Toronto
i have A-B 1769-OW16 output card wired to a contactor with a 1.2A inrush current. i want to connect a surge suppressor parallel to the load (contactor). possibly an MOV (metal Oxide Varistor). any suggestion as to which surge suppressor would be good for this? A-B part number or any manufacturer would be appreciated. thanks!
I would largely base my choice on the design of the terminals of the contactor coil. Most mfg. offer one (surge suppressor) that fits nicely right on the coil terminals, or snaps into the housing with short leads. What is the maker and part number of your contactor?
I have used Quencharc suppressors for a variety of AC controls situations:
http://www.digikey.com/product-highlights/us/en/cornell-dubilier-quencharc-caps/744
They are pretty versatile and reliable in my experience.
use an isolating relay that is enabled by the PLC output is one option
You still should have surge protection to protect the isolating
relays contacts. If the isolating relay is an electro-mechanical
relay ( inductive load) you still should have surge protection to protect the PLC.
I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
111
I have a project to control the speed of motor DC using PWM Output on PLC and when im on working i have a several trouble and of of them is the...
220
Hello, the PLC in question is 1769-L30ER. I have a local 4-20mA Analog Output module (1769-OF4CI), and also a remote ethernet PointIO analog...
400
Hi guys, i have never had to do a PWM Output or input before i have a Device that to dimm the lamp output from the ballast, the ballast has a 24V...
1,051
Hello everyone, I am having issues with an output module connected to my 5069-L306ER PLC. The modules I have connected are a 5069-IA16 in slot 1...
706