hello
i want to communicate PLC 5/30 with weintek MT8104iH HMI with RS232 interface. i have done following setting on plc 9600,8,0,none,crc. serial cable connection are (2 with 3) and
(3 with 2) and (5 with 7). but it is not communicating.
need help
 
Hi,

You will need to provide a little more information to help narrow down your problem. RS232 is your electrical connection - you still need to agree what protocol you will pass over your RS232 connection. Check the Weintek carefully - it has multiple serial ports which are able to be configured for RS232/422/485, depending if you connect to Com1, 2 or 3.

You need to determine what your PLC serial port has been setup for (e.g. DH485 say) before you can successfully talk to the Weintek.
We have used the Weintek HMIs to communicate with several AB controllers using Ethernet, DF1, Modbus and DH485

Regards,

Rob
 

Similar Topics

Dear Expert, Currently I am working in old PLC5 to get the data from Weighing scale delivered by Mettler-Toledo. Here is the result so far: 1...
Replies
2
Views
1,128
I've been searching the forums for hours and I've found many things to try but just haven't found the right answer yet. I have a running PLC 5...
Replies
4
Views
1,871
In one of my project, end-user wants to connect Controllogix 1756 IO's with PLC 5/40E controller on DH+ protocol. 1756 DHRIO card is installed in...
Replies
9
Views
6,742
Hello Friends I need to share some bits between a PLC 5/30 and a 5/04 CPU through DH+.* Is it possible? How can I do that? With MSG...
Replies
4
Views
1,878
I am trying to establish communication between two Allen Bradley PLC5 plcs on dh+ port(which is a three pin connector).Both of them are having...
Replies
5
Views
2,731
Back
Top Bottom