I have an upcoming job where I will need to communicate via Ethernet between a PLC5/40E and an ABB AC800. The ABB is equipped with their PE1364C Modbus to Ethernet IP converter. The literature I have been given for the converter has an example of how to communicate with a ControlLogix processor using CIP Generic type messages. Is this possible with the PLC5? CIP Generic is not an option when configuring a PLC5 message.
My gut feel is that it's not possible, but I want to be sure before telling the client that he needs to buy CLX equipment.
I think that you are correct. The PLC-5E Series F controllers have a nice 10/100BaseT connector on the front, but they still only do "PCCC Encapsulation" for PLC-5 style data exchange with ControlLogix.
The SLC-5/05 recently got a "EEM" Ethernet Explicit Message instruction added with some CIP Generic capability. I doubt the PLC-5 will ever get retrofitted with such a function.
You might get a Digi One IAP to provide the Modbus translation to the PLC-5-specific A-B protocol that you need.
Similar Topics
In one of my project, end-user wants to connect Controllogix 1756 IO's with PLC 5/40E controller on DH+ protocol. 1756 DHRIO card is installed in...
Replies
9
Views
6,739
Hi everyone, I'm a Siemens expert but currently need to do a bit of AB PLC5 work. I have a PLC5/40E. I would like to know if I can add my own N...
Replies
11
Views
2,403
Hello I am troubleshooting a PID. My set output percentage from my SCADA is 60%. However when my PID is in manual my CV is stuck at 20%??? I can...
Replies
8
Views
3,111
Here's a new one for me... Over weekend, one of our plants went on the fritz. On Friday when we closed up everything worked fine, normal...
Replies
4
Views
2,166
Processor PLC5/40E Series E Revision B.2 most his memory, the error log file indicating Error string: "REBOOTp1: hardware fault=0008f at address...
Replies
2
Views
1,461
Back
Top Bottom