Processor PLC5/40E Series E Revision B.2 most his memory, the error log file indicating Error string: "REBOOTp1: hardware fault=0008f at address 3b81e".
Please, help in understanding the reasons
This is a known issue when the users are Online monitoring or forcing I/O located within 32-bit modules over a Ethernet connection; there is no firmware mitigation.
The only suggested recommendation is the use of DH+ user software communications when performing the above mentioned tasks.
I was doing some research and looks like this error is related to was a “BACKGROUND ROM check that failed after power up”, they recommend is to have the controller repaired.