Then to use channel 1A as a remote I/O scanner you must configure the channel for it see picture below. You will also need to edit the chassis properties. see picture below.
Then add your modules to the chassis. Again discrete modules do not need block transfers, they just show up in the data table after you add them to the chassis. Analog module do need "BTR""BTW". The 1794-IE12 and 1794-OE12
are not selectable in the I/O select menu, there are knowledgebase(I.D. 43255 , I.D. 66453) articles about this at AB.com. You need a tech connect contract to view them. ( I don't have one)
http://rockwellautomation.custhelp.com/app/answers/list/kw/1794-oe12/r_id/113025/search/1