Good Mourning
I have a faulted PLC5/V40B processor and I'm having some trouble figuring out what the error code means. It is error code 90 (coprocessor extensive memory test failed). Does anyone know where I could find a more detailed explaination for this fault. I have been digging threw manuals all mouring but have not found much info on this.
This is a VME plc with 2 SST profibus I/O cards (Master and Slave) I believe one of these card may be causing the fault but I cant find enough info to verify this.
Anyone have any ideas?
It's been a while since I've done anything with a PLC5 VME. As I remember that version of PLC5 used a second processor to handle VME and other communications. That may be the memory it is talking about. Are the SST cards VME cards? If so a memory read error from them would act like any other VME memory misread, which shouldn't cause a processor fault. I'm guessing your problem is more internal.
Keith
Keith
Sorry for taking so long to reply I was away from the plant for a few days. The problem seemed to be in the PLC5 processor. Finally found enough information on the SST cards (yes they are VME cards) to troublshoot. I had another PLC5 processor but did'nt want to take a chance on blowing up another $18,000 board.
Other than A.B. do you know of anyone else that can reliably repair these processors? I haven't had much luck getting anything VME repaired.
Thanks for your reply
Hi all, Quick question about maximum RIO for a PLC5. I'm looking to add some a RIO drop that emulates 6 racks to my existing PLC5 system (It is...
1,992
Hello all, I have a question why my Chassis Property display no input or output cards, is it suppose to? For example in the logic , there is a...
951
Hello everyone, I am migrating a PLC5 program controlling a crane to a siemens s7-1500 PLC, but since i have no experience programming PLC5 I have...
2,970
The attached files shows a rung modified by the Migration Tool. Can anyone explain the purpose of the added parallel branch? I figure it has to do...
1,764
I had a customer ask me to investigate what state a digital output would be in a PLC5 if the the processor faulted or was put in program mode...
1,188