Hello group
I had a PLC5/80 with eprom go south. I could not connect through the ethernet and the proc led was solid red. All outputs had been turned off but the plc was in REM mode. I connected through DH+ and I was promted to upload and merge existing project. When I did this, it was some old stuff that I did not recognize. The switches on the plc are not set to burn to eprom. I guess the question is do you think the plc dumped it's memory and I uploaded an original generic project burned into the eprom? My apoligizes if I'm not being very specific, I'm still trying to understand what I'm trying to understand!!
Thanks,
Jeff
The switches you mentioned are used to determine when the PLC READS from the EEPROM. Not write.
The PLC-5 never burns to the EEPROM on it's own. You use the RSLogix5 software to burn the contents of the PLC-5 RAM to the EEPROM.
Sounds like an old program has loaded from the EEPROM to the controller.
OG
Oh no! It sounds like you have caused an old obsolete program to load. I really hope that you have a backup of the actual running program somewhere.....Your tail could really be in a crack now!
I actually changed the processor and downloaded the correct program so I could try and figure out what happened. When I got the plc on the bench I found the odd-ball project. Now I am trying to understand why it dumped it's memory and how the eprom works. It seems that we don't even use the eprom, should I remove it or does that even matter?
I think you have answered your own question. If you don't use it then remove it. Or write the current program to it. ( simple) See PDF below.
The EEPROM IMHO is more of a PITA than anything else when you maintain your batteries and have people on staff who are capable of using RSLogix in case of emergencies.
The advatage to the EEPROM is when you need to be able to restore a processor without goning online, for instance when there are no qualified personnel on hand.
The biggest problem I have had with eeproms is that you must shut down the process in order to save the latest edits to them. If you can do that everytime you make edits to the software and stand to gain from the advantage stated above then keep it.
Also, when the PLC reads from EEPROM, it will overwrite the data tables so you may lose all the settings that have been changed from an HMI/SCADA system.
Look at the status file bits to see how the EEPROM is configured. I can't access RSLogix5, but there should be several choices for how/when to load from eeprom, and also a bit that will tell you when a load from eeprom has occurred.
I would ditch EEPROMS here if given a choice, because keeping up with batteries is pretty foolproof, and reloading a PLC from RSlogix is no problem for me. Our boss likes EEPROMS though and wants us to have one in every machine. I always set them up to only load on memory error, so the only nuiscance for me now is making sure I keep them updated with the latest program edits.
Paul
Thank you for the input and clarification. Mickey I'll hold on to that PDF just in case and thank you. I'm still confused on why we lost the program from that processor. As you can tell I'm just an electromech that has been thrown into the PLC fire, stuff like this is way over my head. (1st time replacing and downloading to controller) I was a bit nervous.
Anyways, thanks again for all the advice that this group gives.
Jeff
Jeff,
The program stored in an EEPROM in a PLC5 will be transferred (or not) depending on your dip swith settings. If your battery gets weak, RAM memory may be lost, and the PLC may try to transfer the EEPROM program, if your chasis DIP switches are both set ON.
DIP Switches:
6 7
ON ON EEPROM memory transfer to PLC-5, if RAM is invalid.
Also check PLC5 Status bits S:2/13, -14, and -15 in your program.
EEPROM S:2/13 - S:2/14
This single field indicates that the EEPROM transfer is either disabled or enabled. It is based on the settings for mutually exclusive bits S:2/13 and S:2/14. Bit 13=1 indicates load from EEPROM enabled. Bit 14=1 indicates RAM backup not configured.
Memory Protection Disabled S:2/15
This indicates Yes or No. Yes means that the EEPROM memory does not transfer to processor memory.
Rockwell Software Inc., 1997, 1998, 1999, 2000
Hi Lancie,Yep, switches 6-7 are open and transfer disabled. I guess I can rule out any eeprom issues. Where did you get that "quote" I've been downloading some very good material from the RA site but have not found anything with that kind of detail.
Thanks again for all the help.
Jeff
Hi all, Quick question about maximum RIO for a PLC5. I'm looking to add some a RIO drop that emulates 6 racks to my existing PLC5 system (It is...
1,993
Hello all, I have a question why my Chassis Property display no input or output cards, is it suppose to? For example in the logic , there is a...
951
Hello everyone, I am migrating a PLC5 program controlling a crane to a siemens s7-1500 PLC, but since i have no experience programming PLC5 I have...
2,970
The attached files shows a rung modified by the Migration Tool. Can anyone explain the purpose of the added parallel branch? I figure it has to do...
1,764
I had a customer ask me to investigate what state a digital output would be in a PLC5 if the the processor faulted or was put in program mode...
1,188