OK so I talked to the customer about a retrofit. They have a 5/40 with digital and analog in the chassis, PF70, and Flex on RIO not sure what all is on the flex network.
So my thoughts are a ControlNet adapter in the local PLC5 chassis. In the CLX chassis a CNB, DHRIO, just for this system. I THINK there are about 5 drives on RIO. Notice I said THINK. I remember hearing that the magic number was 8 or less nodes on a DHRIO card.
So with all that said tell me where I screwed up and what I need to do to fix it before I quote this system.
The PLC will be the easy part.
This is a retro-fit to a running machine?
If so, you need to be more concerned with the drives they are using...much more concerned...That where the finer points of the operation are likely to be handled. Even if you are keeping them, make sure you have copies of all of the parameters, hardware (dipswitch, jumper) settings, and wiring in case something goes awry during the changeover.